D Designer69 Senior Member Nov 25, 2013 #1 Hi guys, looking at a design where the ground bus seems to be mounted directly to the wall (see attached image). I don't understand why not just use the main panelboard ground bus? Maybe I am missing something? Appreciate your help.
Hi guys, looking at a design where the ground bus seems to be mounted directly to the wall (see attached image). I don't understand why not just use the main panelboard ground bus? Maybe I am missing something? Appreciate your help.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Nov 25, 2013 #2 Quite common in commercial buildings especially in service and IT rooms.
iwire Moderator Staff member Location Massachusetts Nov 25, 2013 #3 I agree, I see this done in a lot of large commercial or industrial jobs. It is often used to connect multiple GECs from transformers.
I agree, I see this done in a lot of large commercial or industrial jobs. It is often used to connect multiple GECs from transformers.