Ground bus requirement for electrical closet, Chiller room, IDF and rest room

Status
Not open for further replies.

Leo Li

Member
Location
China
Occupation
Engineer
Hello Sir, when I reveiew US local design firm drawings, I fund there is no ground bus in Chiller room, Electrical closet, IDF, elevator pit and rest room so I gived them comments to add ground bus as bleow, but our design firm replied is " NOT REQUIRED PER US NATIONAL ELECTRIC CODE.". Yes As I checked in NEC thete items clearly to to say "to add ground bus in Chiller room or rest room etc.;..." but I wolud like to know how is these equipment to groud if no local ground bus ? In China all these equipment, electrical panel or rest room metal pipe should be grounded through local ground bus. Thanks in advance!

CHILLER.PNG CLOSET AND REST ROOM.PNG IDF, PIT.PNG
 

Leo Li

Member
Location
China
Occupation
Engineer
You cannot compare our NEC standards to yours. Your design firm is correct.
Thanks, Tom!So I wolud like to know if those equipment metal enclusre ground through feeder ground conductor and no need our called "local repeated ground", correct? And also I want know how to achieve tolilet room metal tube ground?
 

ron

Senior Member
No redundant ground bar is required. Minimum grounding per the NEC is via the equipment grounding conductor (ECG) in the feeder or branch circuit.

I have never heard of a toilet room metal tube ground. Anything in a bathroom that is likely to become energized has an EGC in its circuit and is grounded in that manner.
 

Leo Li

Member
Location
China
Occupation
Engineer
No redundant ground bar is required. Minimum grounding per the NEC is via the equipment grounding conductor (ECG) in the feeder or branch circuit.

I have never heard of a toilet room metal tube ground. Anything in a bathroom that is likely to become energized has an EGC in its circuit and is grounded in that manner.
thanks! So how is those equipment metal enclosure ground such as boiler, Chiller etc.; ? Also through ECG in feeder?
 
  • Like
Reactions: ron

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
All of our circuits require some type of equipment grounding conductor and that EGC is connected to the non-current carrying parts of the electrical equipment.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Perhaps the toilet room metal tube is a metal water line. You’ll need to review art 250 on grounding electrodes to see if the metal tube is an electrode or if not bond per 250.104. If tube is an electrode ground per section 250.66
 
Last edited:

Leo Li

Member
Location
China
Occupation
Engineer
Perhaps the toilet room metal tube is a metal water line. You’ll need to review art 250 on grounding electrodes to see if the metal tube is an electrode or if not bond per 250.104. If tube is an electrode ground per section 250.66
thanks!
 