Ground bus size

Status
Not open for further replies.

Leo Li

Member
Location
China
Occupation
Engineer
HI Friends, is there any code or regulation require that ground bus should be 50% rated current in low voltage switchgear ?Thanks!
 
50%? No. For 4000 amp switchgear and switchboards we typically see 1/4" X 3" copper EGC bus.
 
HI Friends, is there any code or regulation require that ground bus should be 50% rated current in low voltage switchgear ?Thanks!
Leo I firmly believed there was a chart with busbar sizing in gear but I had zero luck finding it or anything related to it except intersystem bonding.

Sorry
 