Ground bushing nec.if liquid tight has metal fittings?

Status
Not open for further replies.
Do they actually make listed metal fittings for non metallic flex?
My supply store has only metal fittings for 1 inch liquid tight they have no plastic fittings. I think they have metal fittings for liquid tight for everything 1 inch and higher like inch and a quarter inch and a half, 2”, etc
 
Do they actually make listed metal fittings for non metallic flex?
AFAIK metallic LT fittings are not listed for use on non metallic LT (even if connecting to metal box). I've also seen way to many times where metal LT fittings have been used non metallic LT to non metallic enclosures thus leaving the metal LT fitting electrically floating.
 
AFAIK metallic LT fittings are not listed for use on non metallic LT (even if connecting to metal box). I've also seen way to many times where metal LT fittings have been used non metallic LT to non metallic enclosures thus leaving the metal LT fitting electrically floating.
If terminated in a metal enclosure, I'll use metal LT fittings with nonmetallic LT every time. The plastic LT fittings are fragile junk.


SceneryDriver
 