UL White Book
METALLIC OUTLET BOXES (QCIT)
CONCENTRIC OR ECCENTRIC KNOCKOUTS
All boxes with concentric or eccentric knockouts have been investigated for bonding and are suitable for bonding without any additional bonding means around concentric (or eccentric) knockouts where used in circuits above or below 250 V, and may be marked as such.
For circuits other than services, the reference in the NEC is 250.97, especially read the second portion of the first sentence of the Exception.
Also remember this is for fairly new boxes, as the "older" boxes would not fall within these parameters and most likely will require some kind of bonding around the eccentric/concentric KOs, for over 250 V circuits.
Reducing Washers, fall under
OUTLET BUSHINGS AND FITTINGS (QCRV)
Metal reducing washers are considered suitable for grounding for use in circuits over and under 250 V and where installed in accordance with the ANSI/NFPA 70, "National Electrical Code". ...for non-service conductors only. Reducing washers may be installed in enclosures provide with concentric or eccentric knockouts, only after all of the concentric and eccentric rings have been removed. However, those enclosures containing concentric and eccentric knockouts that have been listed for bonding purposes may be used with reducing washers without all knockouts being removed.
So, if you are using reducing washers (doughnuts as they are called here in lower NY), be cautious when installing them in existing "older" boxes, as they most likely will require bonding around them.