Ground Bushings

Status
Not open for further replies.

iwire

Moderator
Staff member
Location
Massachusetts
All raceways containing service conductors and in some applications where the voltage exceeds 250 volts to ground.

Take a look at 250.97.
 

iwire

Moderator
Staff member
Location
Massachusetts
Ask me about explosion proof work, or hospitals, I will get that 'dear in the headlights look'. Point being we know what we are used to, if you have not had to worry about it before why would you know it. :)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
In many cases there are other options besides bonding bushings. A bonding wedge or bonding locknut may also be used in many applications where you would use a bonding bushing.
 