Reading up on grounding of mobile equipment. I am curious the take on NEC 250.188 D (see below)? The way I read this is ground fault is required, which is a given. I do not read this to imply ground check is required. But the continuity statement has me curious.
What does the thread community think?
250.188 Grounding of Systems Supplying Portable or Mobile Equipment
(D) Ground-Fault Detection and Relaying
Ground-fault detection and relaying shall be provided to automatically de-energize any component of a system over 1000 volts that has developed a ground fault. The continuity of the equipment grounding conductor shall be continuously monitored so as to automatically de-energize the circuit of the system over 1000 volts to the portable or mobile equipment upon loss of continuity of the equipment grounding conductor.
What does the thread community think?
250.188 Grounding of Systems Supplying Portable or Mobile Equipment
(D) Ground-Fault Detection and Relaying
Ground-fault detection and relaying shall be provided to automatically de-energize any component of a system over 1000 volts that has developed a ground fault. The continuity of the equipment grounding conductor shall be continuously monitored so as to automatically de-energize the circuit of the system over 1000 volts to the portable or mobile equipment upon loss of continuity of the equipment grounding conductor.