ohmhead
Senior Member
- Location
- ORLANDO FLA
Question table 250.122 grounding conductor required to match ampere of phase conductors. Looking at the table in 250.122 i see 100A -200A- 300A if the wire is over but not passed the next higher ampere rage which one do you use? lets say its a 1/0 alu conductor 310.15(b)(16) it calls out at 120amps at 75deg column. Its on a 100Amp breaker can the grounding conductor be a No. 6 alu awg or does it have to be a no. 4 alu awg grounding conductor. Can it be up to but not over 200amps to stay at a No. 6 awg?