Ground Conductor to water pipe

Status
Not open for further replies.

EEC

Senior Member
Location
Maryland
Is there a requirement to install ground wire from mobile generator to water pipe on 208/120Y system? Or can the ground wires from generator attach too service ground wire at switchboard? What qualifies as a SDS? Since it mobile, consider it temporary.
 
Is this generator temporary or permanent?
Is it for Art 700, 701, or 702?

You should read the definition of Separately Derived System. You may need to take a look at 250.34/250.30.

Maybe you could be more specific in your post and a more detailed answer could be provided.
 