A Alwayslearningelec Senior Member Location NJ Occupation Estimator May 11, 2021 #1 Would you need to add a ground as they indicate? It's from the utility manhole to the service switch. HDPE is a non metallic pipe so I'm assuming a ground is needed. 3 phase 120/208v service Attachments Capture.JPG 118.1 KB · Views: 15
Would you need to add a ground as they indicate? It's from the utility manhole to the service switch. HDPE is a non metallic pipe so I'm assuming a ground is needed. 3 phase 120/208v service
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician May 11, 2021 #2 No there is no EGC required (or permitted) for service entrance conductors. You only need the 4 conductors mentioned in the note.
No there is no EGC required (or permitted) for service entrance conductors. You only need the 4 conductors mentioned in the note.