250.122 (F)(1) and then 250.122(B)?
Take a very long run (over 1000') for a 2000A 480/277V feed from a 4000A main service switchboard to 2000A switchboard. (don't punish the engineer - the owner will not accept medium voltage - just go with me on this)
To make voltage drop work, you move up from (5) 4" C. to (10) 4" C., each with (4) 600KCMIL, (plus ground). An easy 100% increase in the ungrounded conductor size.
Table 250.122 says use 250KCMIL for 2000A device.
Q#1 - Do you need to upsize 100% to 500KCMIL in each of the 10 pipes?
[It does seem extreme, being you already have 250x10=2500KCMIL of copper ground...to have to go up to 500x10=50000KCMIL of copper ground./
Q#2 - Is the only way around this to put ground fault protection on the main switchboard 2000A branch breaker? Using 250-122 (F)(2)