Is this a solution in search of a problem? Is it a solution at all?
Let’s say you want to find out which way power is flowing through a #14 ground conductor 100’ long, and it’s not Direct Current so you can’t check the current direction.
The power is supposed to go into the ground, right?
But suppose due of other current paths and PoCo, the power is coming out of the ground and into the load.
How can you tell?
As a last resort, put a 1/4 ohm resistor between the ground connection and the conductor. The ground current will be halved by this and hopefully this does not screw things up.
With respect to the ground rod connection, measure the voltage on other end of the resistor and
on the other end of the ground conductor (use an extension cord conductor or a long, skinny wire as a test lead).
If the power is going into the ground, this last voltage will be the higher one.
Otherwise the power is coming out, with the ungrounded end of the resistor having the higher AC voltage.
Depending on the ground conductor current, small voltage differences may be hard to resolve (I’ve never done this).
For a 10A ground conductor current the resistor needs to dissipate 25w. 60’ or so of #16 or less length of a smaller gauge will probably work for the resistor.
The wire will heat up and change resistance but this change may be negligible for a 1 or 2 second test duration.
A better choice is a length of Nichrome wire, if you can find it.
Let’s say you want to find out which way power is flowing through a #14 ground conductor 100’ long, and it’s not Direct Current so you can’t check the current direction.
The power is supposed to go into the ground, right?
But suppose due of other current paths and PoCo, the power is coming out of the ground and into the load.
How can you tell?
As a last resort, put a 1/4 ohm resistor between the ground connection and the conductor. The ground current will be halved by this and hopefully this does not screw things up.
With respect to the ground rod connection, measure the voltage on other end of the resistor and
on the other end of the ground conductor (use an extension cord conductor or a long, skinny wire as a test lead).
If the power is going into the ground, this last voltage will be the higher one.
Otherwise the power is coming out, with the ungrounded end of the resistor having the higher AC voltage.
Depending on the ground conductor current, small voltage differences may be hard to resolve (I’ve never done this).
For a 10A ground conductor current the resistor needs to dissipate 25w. 60’ or so of #16 or less length of a smaller gauge will probably work for the resistor.
The wire will heat up and change resistance but this change may be negligible for a 1 or 2 second test duration.
A better choice is a length of Nichrome wire, if you can find it.