Greetings, Gents
When installing new panels/metal enclosures, how important is it to perform continuity test on the bonding wire to make sure it's tied to existing GES that is continuous? For example, say we are adding a panel and installing EGC from the panel to the existing system grounding conductor. If the grounding conductor in question is open circuit and not tied to the ground source of the system, then we've effectively not grounded the panel. In existing installation where the ground grid system may be suspect, specially in generating/industrial facilities, it seems prudent to test making sure the EGC is continuous all the way back to where the system bonding jumper is installed.
Am I correct in my approach?
Thanks,
EE
When installing new panels/metal enclosures, how important is it to perform continuity test on the bonding wire to make sure it's tied to existing GES that is continuous? For example, say we are adding a panel and installing EGC from the panel to the existing system grounding conductor. If the grounding conductor in question is open circuit and not tied to the ground source of the system, then we've effectively not grounded the panel. In existing installation where the ground grid system may be suspect, specially in generating/industrial facilities, it seems prudent to test making sure the EGC is continuous all the way back to where the system bonding jumper is installed.
Am I correct in my approach?
Thanks,
EE