I was asked to consult on a problem with excessive grounding conductor current on a group of new APC UPS systems. A testing company measured 26 amps on the grounding conductor. When the generator was running, the current increased to over 50 amps.
The systems is fed with a 2000 amp three wire 480 volt switchgear.
On a closer inspection - the APC equipment had both neutral and ground busses and they were jumpered which solved the problem.
The problem is, installation of a neutral will cost many thousand of dollars. APC states that there is no need for a neutral and that that it is normal for the ground to carry the measured current. In fact, in the letter to the customer from Schnieder (Square D , APC) they state that this grounding conductor is totally safe and normal and "harmless". They state in the letter that their equipment is properly installed for a three wire system (tying the neutral bus to the ground bus and using the grounding conductor and ground system to carry unbalanced harmonics current).
This equipment is in a very critical data center in a hospital.
I still maintain that they have a serious problem and do not meet code but I am being overuled.
Any comments?
The systems is fed with a 2000 amp three wire 480 volt switchgear.
On a closer inspection - the APC equipment had both neutral and ground busses and they were jumpered which solved the problem.
The problem is, installation of a neutral will cost many thousand of dollars. APC states that there is no need for a neutral and that that it is normal for the ground to carry the measured current. In fact, in the letter to the customer from Schnieder (Square D , APC) they state that this grounding conductor is totally safe and normal and "harmless". They state in the letter that their equipment is properly installed for a three wire system (tying the neutral bus to the ground bus and using the grounding conductor and ground system to carry unbalanced harmonics current).
This equipment is in a very critical data center in a hospital.
I still maintain that they have a serious problem and do not meet code but I am being overuled.
Any comments?