Ground fault 4000 amp GE power Break 1, Manual type

Fordean

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
Had a call on a 4000 amp Main breaker. It has tripped 2 times. This past tuesday. and 6 months ago.
Happened at 200 am, They company employees Tried to Reset breaker. But after charge, Would not close, And remained open. And 3 attempts 2 hr later,
It finally reset.
I viewed the screen on the Microversa Trip plus trip unit. And it looks to have a error code displayed, .23 I believe GF code, Which is ground fault. Any input,

They want to remove this breaker. And replaced.

GE TP4040TR Power break 1 type.
4000 amp CT Chip in Micro switch
Microversa Trip plus trip unit
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I had a similar call from an insurance company headquarters.
The GF setting of the main had never been coordinated with downstream branch breakers. When set to minimum it would trip before a 30A branch breaker. So this was the first thing we 'adjusted' followed by field testing, before replacing the breaker.

The GF was eventually traced to a new set of duct heaters, when enough banks were on the system faulted, when only one or two banks were on things ran fine.
 