timm333
Senior Member
- Location
- Minneapolis, MN
- Occupation
- Electrical Design Engineer
I have a question about the ground fault coordination time interval. The phase protection of LV breaker is coordinated with upstream MV phase 50/51 relay with a time delay of 0.22 sec. And the ground protection of LV breaker is coordinated with upstream MV ground 50G/51G relay with a time delay of 0.1 sec.
Do we also need to provide the coordination of the ground protection of LV breaker with the upstream phase 50/51 relay, what should be the time delay in this case? Thanks
Do we also need to provide the coordination of the ground protection of LV breaker with the upstream phase 50/51 relay, what should be the time delay in this case? Thanks