Question: Can the ground fault current be used as "minimum short circuit current" for arc flash hazard calculations?
Background: I received a power system study in SKM for review and saw that the 3rd party engineering company used the ground fault current, provided by the local utility company as the minimum fault current while the bolted fault current was used as the maximum fault current.
System configuration and equipment: GF and bolted fault are provided on the primary side of a 3000kVA transformer. 12470 /480 V. System configuration is delta / wye solidly grounded. The secondary protection in an obsolete fused switchboard is provided through a virtual main with 50/51 activated only. Yes, there is no GFP activated or installed. And yes, I am aware that this is not code compliant also considering that this is a research facility.
The fault is interrupted through a vacuum fault interrupter w/ load break switch. The site acceptance test showed a fault clearing time of 60ms (3.5 cycles). The question is, will the current transformers for the virtual main pick up on the ground fault current?
I assume yes, since the GF current will flow back to the system but any opinion is welcome.
Background: I received a power system study in SKM for review and saw that the 3rd party engineering company used the ground fault current, provided by the local utility company as the minimum fault current while the bolted fault current was used as the maximum fault current.
System configuration and equipment: GF and bolted fault are provided on the primary side of a 3000kVA transformer. 12470 /480 V. System configuration is delta / wye solidly grounded. The secondary protection in an obsolete fused switchboard is provided through a virtual main with 50/51 activated only. Yes, there is no GFP activated or installed. And yes, I am aware that this is not code compliant also considering that this is a research facility.
The fault is interrupted through a vacuum fault interrupter w/ load break switch. The site acceptance test showed a fault clearing time of 60ms (3.5 cycles). The question is, will the current transformers for the virtual main pick up on the ground fault current?
I assume yes, since the GF current will flow back to the system but any opinion is welcome.