Can I put 20A GFEP breakers inside my breaker box? This would only be going to 2 outside receptacles. And where in the NEC book can i find this? I dont see it. hmy:
You can protect your outside outlets by a GFCI circuit breaker in lieu of a GFCI receptacles itself.
Breakers are available for most panels (a few of the extinct panels such as FP, Zinsco and Pushmatic are exceptions)
GF protection for equipment (GFP) has a much higher threshold (such as 30ma to hundreds of amps) than that required for personnel(5 ma)