In one of the provision in article 240, there is an exemption that fire pump may not have ground fault protection. Will this be more dangerous because a ground fault is a short circuit fault for a solidly grounded system. The code is not clear and this may result to further burning of the establishment if ground fault protection for fire pump will be removed.
The code should emphasized that for a fire pump to have no ground fault protection the system should be either UNGROUNDED OR HIGH IMPEDANCE GROUNDED. Or if the existing system is SOLIDLY GROUNDED then an isolation transformer should be used to convert the Solidly grounded to either ungrounded or high impedance grounded.
The code should emphasized that for a fire pump to have no ground fault protection the system should be either UNGROUNDED OR HIGH IMPEDANCE GROUNDED. Or if the existing system is SOLIDLY GROUNDED then an isolation transformer should be used to convert the Solidly grounded to either ungrounded or high impedance grounded.