I asked my apprenticeship instructor if a groung fault rec. will work on a circuit that is arc fault protected. He told me to figure it out. Any ideas?
Filthy Phil said:Thanks. He isn't a very good teacher. He usually just yells, and if you don't understand, he just yells louder.
Are you paying this teacher to yell at you?Filthy Phil said:Thanks. He isn't a very good teacher. He usually just yells, and if you don't understand, he just yells louder.
Filthy Phil said:I asked my apprenticeship instructor if a groung fault rec. will work on a circuit that is arc fault protected. He told me to figure it out. Any ideas?
According to the AFCI people that is not the type of arc fault that the AFCI looks for. That is a series arcing fault and the AFCIs only directly detect parallel arcing faults. They detect poor connections or series arcing faults when the heat from the fault causes enough damage so that the fault becomes a ground fault or a parallel arcing fault.Arcing faults occur when a connection loosens.
don_resqcapt19 said:According to the AFCI people that is not the type of arc fault that the AFCI looks for. That is a series arcing fault and the AFCIs only directly detect parallel arcing faults. They detect poor connections or series arcing faults when the heat from the fault causes enough damage so that the fault becomes a ground fault or a parallel arcing fault.
Don
don_resqcapt19 said:According to the AFCI people that is not the type of arc fault that the AFCI looks for. That is a series arcing fault and the AFCIs only directly detect parallel arcing faults. They detect poor connections or series arcing faults when the heat from the fault causes enough damage so that the fault becomes a ground fault or a parallel arcing fault.
Don
They do not release that type of information.Could you please let them supply you with the detailed technical explanation of how do they accomplish this and post it here.
This device was strongly pushed by the CPSC, and of course the manufacturers.It would be also helpfull if they can furnish you with the historical origin of the problem that generated the development of this device.
I am not convinced that is the case, especially since the AFCI people went to great lengths a few years ago to say that a series arc is not even possible at dwelling unit voltages.Jan 1st the AFCI requirement changes to include combination arc fault that includes series arching.
don_resqcapt19 said:I am not convinced that is the case, especially since the AFCI people went to great lengths a few years ago to say that a series arc is not even possible at dwelling unit voltages.
Don
don_resqcapt19 said:Energize,
I really don't care what the manufacturers say about AFCIs...they have lied from day one on this issue. Their original proposals some 13 years ago said that the device they had back then would do everything that the combination type is said to do and the combination type is just getting to the market now.
Jan 1st the AFCI requirement changes to include combination arc fault that includes series arching.
I am not convinced that is the case,
especially since the AFCI people went to great lengths a few years ago to say that a series arc is not even possible at dwelling unit voltages