mshields
Senior Member
- Location
- Boston, MA
Much of my career has been in the healthcare arena where ground fault on 1000A and higher plus a second level (480V systems) is not negotiable unless on LS and Critical branches. But I recently had occasion to review 215.10 for a non-hospital. And tell me, does Exception 2 mean that if you have say a 3000A service circuit breaker for a building which requires Ground fault protection per 230.95, that you don’t need it on a feeder breaker on the main board rated for 1000A or more (assuming all of the above is on a 480V system). If so, how often would GF be mandated on feeders. I mean, wouldn’t this be a fairly typical scenario. And if so, doesn’t the exception in this case, become, more often than not, the rule?