What happens on an ungrounded MV delta delta 2000kVA XFMR - 3 ph 3 wire if there is a ground fault and the XFMR secondary DOES NOT HAVE A GEC?
 
What about the Nec requirement 250.30(B)?


Enviado desde mi iPhone utilizando Tapatalk
The GEC and the EGCs on an ungrounded system are there to provide a fault clearing path when there is a second ground fault. They really don't do anything else on an ungrounded system.
 
We can’t guess - Nec requires it for a reason


Enviado desde mi iPhone utilizando Tapatalk
Electrical equipment is bonded to ground to reduce damage from nearby lightning strikes. In a grounded system, it also serves as a path to trip an OCPD in case an ungrounded phase becomes grounded.

But "What happens to an Article (when whatever happens) ?" I guess I don't understand the grammar. Like, does that page in the NEC catch fire or something?
 
The GEC and the EGCs on an ungrounded system are there to provide a fault clearing path when there is a second ground fault. They really don't do anything else on an ungrounded system.

Don, it appears the GEC can also be installed at the downstream switchgear if I’m reading 250.30(B)(1) correctly. Both are located indoors and within a few feet of each other.


Enviado desde mi iPhone utilizando Tapatalk
 