Recently we have a 500HP, 4160V, 3-PH motor (drives a water pump) that keeps tripping "Ground Fault" via a digital protection relay on motor start-up. Below are some parameters first (also see drawing illustration):
Ground Fault CT type: zero-flux CT (around 3 phase conductors)
CT Ratio: 2000:1
Ground Fault trip at: 2 amps primary
Ground Fault trip delay: 1 second
Motor FLA: 60amps (500HP, 4160V)
Electricians observed that motor was able to start and come over the inrush for the first few seconds--motor amp pegged out first and then dropped to around 15 amps on each phase, then after 3 seconds or so, motor tripped on "Ground Fault" through the digital relay.
This is a fairly old type digital relay, so I'm not able to see exactly how much the "ground fault" current was.
Motor was megged from the starter end with 2.5G ohms on each phase to ground.
Questionable point to me is that how could the motor amps get down so low?. Also, would this ground fault CT configuration also trip on imbalance? The CT is vectorly summing the three-phase current, so any imbalance would cause the summation to a value other than zero?
At this point, I'm not sure this is truly a motor issue. Pump/motor was coupled up with another steam drive (dual drive set-up); however this problem occured when the steam drive is uncoupled, so just motor driving the pump.
Any ideas fellas?
Ground Fault CT type: zero-flux CT (around 3 phase conductors)
CT Ratio: 2000:1
Ground Fault trip at: 2 amps primary
Ground Fault trip delay: 1 second
Motor FLA: 60amps (500HP, 4160V)
Electricians observed that motor was able to start and come over the inrush for the first few seconds--motor amp pegged out first and then dropped to around 15 amps on each phase, then after 3 seconds or so, motor tripped on "Ground Fault" through the digital relay.
This is a fairly old type digital relay, so I'm not able to see exactly how much the "ground fault" current was.
Motor was megged from the starter end with 2.5G ohms on each phase to ground.
Questionable point to me is that how could the motor amps get down so low?. Also, would this ground fault CT configuration also trip on imbalance? The CT is vectorly summing the three-phase current, so any imbalance would cause the summation to a value other than zero?
At this point, I'm not sure this is truly a motor issue. Pump/motor was coupled up with another steam drive (dual drive set-up); however this problem occured when the steam drive is uncoupled, so just motor driving the pump.
Any ideas fellas?