Ground-Fault Protection 230.95

Status
Not open for further replies.

abcclub

Member
Does a 480 volt 4,000 amp service that employs a high impedance grounded neutral still required Ground-fault protection?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
I think not. Right up front, that article says it applies to solidly grounded wye systems.
 

brian john

Senior Member
Location
Leesburg, VA
With the high impedance you would never achieve the currents high enough to trip the standard GFP relay 100-1200 Amps. In addition the typical use of a high impedance system is to minimize outages from ground faults.
 