Are you saying you had a ground fault and you are trying to isolate this possible ground fault?
Yes.
1. What features does the CB OCP have Long time? Short time? Instantaneous? GFP?
Long Time range= 1 to 4, set at 4
Instantaneous range= 1.5x to 10x, set at 3x
Current range= .5 to 1.0, set at 1.0
GF Pickup range= .25 to .375, set at .375
GF Delay range= I2T In / I2T Out, set to I2T Out Max
2. What makes you think it was a GFP operation?
Relatively low current draw, not measured, expect that it was 400 to 600 amps max, likely less.
Older building customer is moving into. Found many EGCs on neutral bars, most have been placed on new EGC terminals, not all yet.
3.Can you get someone to perform Secondary injection or primary injection testing?
IDK. Is that generally done on site or would that be sent out? If the pickup is faulty, is that the only reasonable way to find out? Thousands?
4. Did you or someone else reset the CB without determining the cause of the fault?
Yes.
5. Did you check all downstream motors (Megger)?
Not yet. One recently for other concerns, ok.
6. Did you megger the feeder?
Not yet. I plan to start from load sides of fused switches in switchgear, and work downstream. Thought I would skip the busbars within switchgear to start, but can go back to them after one or two levels of tracing.
7. Did you check for downstream OCP (fuses or CB's) tripped/blown?
Yes. Large building, checked many, less than all.
8. Were there any contractors working in the building doing renovations possibly tripping a 480/277 CB accidentally or intentionally.
Not really. The customer is still setting up, so some tools as a contractor would use, but few at the time. None of the large production equipment in use to my knowledge at that time, but circuits were energized.
9. What is the GFP settings?
As above.
10. If the system is back on can you measure the current on the neutral ground bond?
Unsure. I mean, yes, eventually, but want to have POCO deenergize to so we can maintain 13k disconnect outside before operating such. I doubt it has been used in 23 years. So a lot of coordination will be needed. Don't want to open main section hot . . . The service feeds a second main (208 wye), so they will lose power to that when service is opened. I want to postpone that as long as reasonable.
11. Did you megger the neutral to ground with the bond lifted.
Not 'till as above.
Can you explain these settings? Is the GF Pickup a percentage of the total OCP level, or of the 1200a permitted (now and in 1984)?
What current level of GF might we be seeing?
What is the difference between the Long Time Delay and the GF Delay? Is the Long for simple overcurrent?
Thanks.