Here is summary of my application:
Utility is feeding a 500kVA Step down transformer from 16kV to 2.4kV feeding 2.4kV overhead distribution circuit with a Delta Detla Configuration. connected loads are 2.4kV-480/277V step down transformers feeding 480V loads
Goal is to install a ground fault protection device per utility requirement: For the customer service disconnect recloser to be installed on the pole on the 2.4kV system.
prior to the main questions please correct my analysis:
Ground Fault Detection: Install the PT's (2.4kV-120V) connect the primary in Wye and secondary in broken Delta. The voltage developed across the broken delta of the PT's will be 3V0 (Zero Sequence Voltage-any unbalance in the Voltage). can some body help me calculate manually how much this phase unbalance will be for a loss of one of the phases? so that i can enable the relays only for a loss of phase instead of the unbalance voltage in the phases. using this voltage i can pickup a contact from a relay and use it in the recloser to trip.
Disadvantage is entire facility will be down.
Option2:
High resistance Ground: This is actually similar to the delta delta system only advantage of HRG is it will tell you when there is ground fault where as in delta delta it don't. there is no interruption in the service. Also no high voltage stress ( Phase to Phase Voltages) appeared in the on the phase to ground connected loads.
Please pull me out of this grounding well.......
Thanks in advance for the input.
Utility is feeding a 500kVA Step down transformer from 16kV to 2.4kV feeding 2.4kV overhead distribution circuit with a Delta Detla Configuration. connected loads are 2.4kV-480/277V step down transformers feeding 480V loads
Goal is to install a ground fault protection device per utility requirement: For the customer service disconnect recloser to be installed on the pole on the 2.4kV system.
prior to the main questions please correct my analysis:
- If there is a single phase to ground fault in the system any loads connected on line to ground (which is 2.4kV/1.732=1.38kV) will be under stress of high voltage (which is 2.4kV line to line Voltage). If all the connected loads are rated for the 2.4kV insulation and higher there should be any trouble for single phase faults.
- In a Delta Delta system since for the ground fault there is no return path to source there is very minimal fault current and load remains running normal conditions if so why do i need a ground fault protection. Note: Is this because of most single phase faults lead into 2 phase and 3 phase faults. If so my recloser will trip for the 2 phase and 3 phase faults anyway as over current protection will be enabled.
Ground Fault Detection: Install the PT's (2.4kV-120V) connect the primary in Wye and secondary in broken Delta. The voltage developed across the broken delta of the PT's will be 3V0 (Zero Sequence Voltage-any unbalance in the Voltage). can some body help me calculate manually how much this phase unbalance will be for a loss of one of the phases? so that i can enable the relays only for a loss of phase instead of the unbalance voltage in the phases. using this voltage i can pickup a contact from a relay and use it in the recloser to trip.
Disadvantage is entire facility will be down.
Option2:
High resistance Ground: This is actually similar to the delta delta system only advantage of HRG is it will tell you when there is ground fault where as in delta delta it don't. there is no interruption in the service. Also no high voltage stress ( Phase to Phase Voltages) appeared in the on the phase to ground connected loads.
Please pull me out of this grounding well.......
Thanks in advance for the input.