On one of my projects, I noticed that there was a large bus-duct with several disconnects plugged in.
This was a 3 phase 480 Volt busway, fed from a bank of (3)- 500 kVA transformers. There were several 225 Amp disconnects which also had a junction box mounted above them. Inside that box was a CT device connected to a shunt-trip mechanism in the disconnecting breakers. It appeared to be some sort of Ground-fault protective device for equipment.
Is this required? I thought that the ground-fault protection for equipment was only required on larger (over 1000 Amp) feeders and services? According to my calculations, that transformer bank would produce just over 600 Amps at full capacity.....
This was a 3 phase 480 Volt busway, fed from a bank of (3)- 500 kVA transformers. There were several 225 Amp disconnects which also had a junction box mounted above them. Inside that box was a CT device connected to a shunt-trip mechanism in the disconnecting breakers. It appeared to be some sort of Ground-fault protective device for equipment.
Is this required? I thought that the ground-fault protection for equipment was only required on larger (over 1000 Amp) feeders and services? According to my calculations, that transformer bank would produce just over 600 Amps at full capacity.....