Some GE Micro Versa Trip units can have false GF trips on high inrush currents, especially if harmonics are involved. It usually occurs if the trip unit is wired for a 3-phase, 3-wire system, like it would be for a motor feeder with no neutral wire. The trip unit still has a neutral CT input on the circuit board, even though there is no connection to it. The open input picks up noise during high inrush currents and fools the GF circuit into tripping.
In our case, GE field service tested the units and declared they were good, twice. We finally brought in 50kA test sets from a NETA company and cranked high phase-phase current through the breakers proving the trip units would false trip on high currents. We found the problem on multiple breakers, vintage 2002.
More likely, your problem is related to the harmonics. A change to a fancier trip unit may be needed to get a true RMS sensing device. Or defeat the GF on the breaker, add a shunt trip, donut CT and an external GF relay.