It is hard to coordinate a single level of GF with branch breakers as small as 70A. This results in faults on branch circuits taking out the whole service. My preference is to add GF on all feeders with adjustable tripsBeen working on high-rise project for several months. I have attached a partial one line diagram. I don't know how I missed this but I believe the 2000/3p disconnect show on MSB-1 and 2 will require GF sensing. Is that correct?
Dan Craven
Not according to your one line. It is a 480/277 system.No that is 208/120 service.
The disconnects in question are probably not service disconnects, but there are analogous requirements in articles 210 and 215.Yes. Refer to the following code section.
"230.95 Ground-Fault Protection of Equipment. Ground-fault protection of equipment shall be provided for solidly grounded wye electric services of more than 150 volts to ground but not exceeding 1000 volts phase-to-phase for each service disconnect rated 1000 amperes or more. "
They appear to be service disconnects given the location of the utility metering and the fire pump connections.The disconnects in question are probably not service disconnects, but there are analogous requirements in articles 210 and 215.
I believe GFPE and arc energy reduction would apply for each of the 2000A breakers.Note 20 only says it a 100% rated breaker.
But the 4000 amp breakers are on the secondary of transformers that have a 480 volt primary.Not according to your one line. It is a 480/277 system.
I don't understand the context of your statement. The OP was asking about the 2000A breakers not the 4000ABut the 4000 amp breakers are on the secondary of transformers that have a 480 volt primary
The 2000A breakers require GFP per the NEC. The code section is 230.95 in the 2020 NECJust to be clear. The 2000amp breakers on MSB-1 & 2 feed a 480-120/208 transformer with bus duct risers for multi metered sections per floor.
Good point. So is this a situation where the utility has a 208 network distribution and is supplying the transformers to supply 480?They appear to be service disconnects given the location of the utility metering and the fire pump connections.
I believe it's the opposite. The service is 480Y/277.Good
Good point. So is this a situation where the utility has a 208 network distribution and is supplying the transformers to supply 480?