Ground Fault Protection of Equipment

Location
St. Louis, missouri
Occupation
Electrical Engineer
Been working on high-rise project for several months. I have attached a partial one line diagram. I don't know how I missed this but I believe the 2000/3p disconnect show on MSB-1 and 2 will require GF sensing. Is that correct?

Dan Craven
 

Attachments

  • Partial One Line Diagram.pdf
    46.5 KB · Views: 9
Been working on high-rise project for several months. I have attached a partial one line diagram. I don't know how I missed this but I believe the 2000/3p disconnect show on MSB-1 and 2 will require GF sensing. Is that correct?

Dan Craven
It is hard to coordinate a single level of GF with branch breakers as small as 70A. This results in faults on branch circuits taking out the whole service. My preference is to add GF on all feeders with adjustable trips
 
Yes. Refer to the following code section.


"230.95 Ground-Fault Protection of Equipment. Ground-fault protection of equipment shall be provided for solidly grounded wye electric services of more than 150 volts to ground but not exceeding 1000 volts phase-to-phase for each service disconnect rated 1000 amperes or more. "
 
Yes. Refer to the following code section.


"230.95 Ground-Fault Protection of Equipment. Ground-fault protection of equipment shall be provided for solidly grounded wye electric services of more than 150 volts to ground but not exceeding 1000 volts phase-to-phase for each service disconnect rated 1000 amperes or more. "
The disconnects in question are probably not service disconnects, but there are analogous requirements in articles 210 and 215.
 
Top