Ground fault protection required at main service?

Status
Not open for further replies.

anbm

Senior Member
Location
TX
Occupation
Designer
208Y/120V main service panel, wye connection, 4Wires +Ground, 1600A main breaker.

NEC 230-95 requires ground fault protection for solidly grounded wye electric service of more than 150V to ground.

The voltage to ground for above panel is 120V, so above rule won't apply?
 
208Y/120V main service panel, wye connection, 4Wires +Ground, 1600A main breaker.

NEC 230-95 requires ground fault protection for solidly grounded wye electric service of more than 150V to ground.

The voltage to ground for above panel is 120V, so above rule won't apply?

you are correct

But I notice that you use the - in your code referance, that was last used in 1999 code issue, for 2002 and later it should be a dot.
Like 230.95
 