Ground Fault Protection Tripping Main
strap89
Hello,
I'm having a main trip intermittently, presumably the ground fault protection is the culprit. Service is sized more than adequately. This is a 2500A service with a ground fault trip setting of 200A. My first instinct was that a load imbalance was being mistaken for a ground fault condition, but I am starting to think that this may not be a possibility. It's my understanding that the vectoral sum of the phase currents will equal zero unless regardless of which sensing method used. Is this a correct assumption?
My thoughts are possibly an actual ground fault, or maybe an incorrectly wired CT? Any thoughts or input would be appreciated.
More specifically on the incorrectly wired CT hypothesis, I think the service is using a source ground sensing configuration. I would assume the ground sensing CT if wired backwards would read a positive ground fault condition even with an imbalanced load?
If the GFP is sensing all ungrounded and grounded conductors, then the sum will be 0 unless the current is going on the grounding system/conductor somewhere. Some GFP only senses the ungrounded conductor, so a sever imbalance could be misinterpreted as a GF.
You should check the main GF setting with the phase setting of your downstream breakers. Many people forget to do this.
Based on a 200A setting I would guess your main will trip before a 30A branch breaker. The result is that a miswired or faulted duct heater could trip your GF now that heating season is upon us.
If you only have GF at the main it will be likely that you can only coordinate up to about a 70A branch.
Seen it happen more than once with 277 volt ballasts, where the ground fault setting for the main was left at the factory minimum because the designers had never specified the correct setting. Typically this would be long after the project had been completed, when the ballasts started to fail.
I always had my engineers show a common 30A breaker on the same TCC plot as any GF. I felt this was typically the maximum size circuit that people tended to work on while energized, like when changing ballasts or switches.
For some reason our industry shies away from GF whenever possible, usually resulting in a single level of protection and these main breaker "nuisance" trips. It must be more profitable to troubleshoot these trips than it is to prevent them in the first place.
Probably liability. If a fire happens because of a ground fault, and it’s not at minimum, the finger gets pointed at the electrician, or if it’s in the specs, the engineer.
Most of the time it’s doing its job, ground fault in the parking lot lighting, bad second stage A/C compressor or heat strips. The big box store maintenance departments would want us to turn it all the way up.
I agree, you should not just 'click and go', someone needs to make a conscious decision which settings are appropriate.
I would think a professional contractor would still be liable for blindly following an unqualified customer that says 'crank 'er to the maximum'.
Thanks everyone. Coordinated the upstream and downstream breaker ground faults to try to isolate the ground fault and it still tripped the main. Main was set to 400A and the lower levels were set to 240A. Main delay was set longer than the sub panels. It definitely is not an overload condition. Leaning towards an incorrectly wired CT, either open, backwards, or the neutral is not passing through the CT.
Or possibly the CT not connected. Some are set up with a large CT that is mounted to where all conductors pass through, I’ve seen one where one of the parallel conductors was short, and was routed outside the ct, so every time a large air compressor started, it tripped on ground fault. Had another where it had a separate CT that was buss mounted, and installed backwards. Another one the CT was installed, but was not wired to the input terminal on the breaker. If the system has been working for years, those situations are probably not the cause. If it’s recently colder, and trips when the heat is at the peak, most likely a second stage heat fault, or if it’s only does it at dark, especially after a rain, it could be a fault in the parking lot. Either an underground splice, or bad ballast.
So, it turns out it was a lighting fixture that was causing the ground fault. They had not set the downstream protection as advised, so they were able to correct and isolate the ground fault to the floor. They then determined it was one or two fixtures causing the issue. What I can't seem to wrap my head around is why the 20A breaker didn't trip first. The upstream ground fault delays definitely coordinate with the smaller 20A/1P breaker.
Happens quite often, especially if the circuit is long. It’s usually not a bolted fault, but a high resistance fault, such as a ballast winding. A couple hundred amps will not instantly trip a 20 amp breaker, with the ground fault setting low, along with a short delay setting, the main picks it up quicker.