Hello,
I'm having a main trip intermittently, presumably the ground fault protection is the culprit. Service is sized more than adequately. This is a 2500A service with a ground fault trip setting of 200A. My first instinct was that a load imbalance was being mistaken for a ground fault condition, but I am starting to think that this may not be a possibility. It's my understanding that the vectoral sum of the phase currents will equal zero unless regardless of which sensing method used. Is this a correct assumption?
My thoughts are possibly an actual ground fault, or maybe an incorrectly wired CT? Any thoughts or input would be appreciated.
I'm having a main trip intermittently, presumably the ground fault protection is the culprit. Service is sized more than adequately. This is a 2500A service with a ground fault trip setting of 200A. My first instinct was that a load imbalance was being mistaken for a ground fault condition, but I am starting to think that this may not be a possibility. It's my understanding that the vectoral sum of the phase currents will equal zero unless regardless of which sensing method used. Is this a correct assumption?