Ground Fault Protection

Status
Not open for further replies.

Sajid khan

Senior Member
Location
Pakistan
Article 517.17 Require Ground fault protection on a breaker rating greater than 1000A.
May i know what can be the consequences if ground fault is not used??

Thanks


Sent from my iPhone using Tapatalk
 
With services of that size, sustained arcing ground faults are possible. This means that an arc forms from phase to ground, but the current flow is low enough that ocpd doesn't trip.

So a fault can turn the electrical system into an arc furnace which consumes itself and everything around it......

Jon
 
Article 517.17 Require Ground fault protection on a breaker rating greater than 1000A.
May i know what can be the consequences if ground fault is not used??

Thanks


Sent from my iPhone using Tapatalk
 
At 120 volts there is not enough energy to sustain an arcing fault. A 277 arcing fault will not extinguish. Somewhere I have a picture of MRS that was melted from a arcing fault.
 
It does the same thing a GFCI does that a breaker can't, except for equipment instead of people.
 