To put it politely, grounding is one of the most pervasive and least understood parts of the electrical system. To put something in the Code you have to among other things show a need for it these days. Some sort of documentation of the risk. And show that it’s feasible. Also although it is quickly getting away from this, electricians are supposed to follow Code. If it turns into an engineering project there better be a very good reason. The one line arc flash rule is still a huge issue and the SCCR rules aren’t much better.
Most of the time on smaller loads for instance phase overcurrent does double duty. And if we introduce it, pray tell how are you going to do coordination? And how to check coordination between the two? Without a $10,000 software program and a $5,000 engineering study for every house built? And if so, what’s the risk? That’s why the rule for roughly 1,000 A and over is totally inadequate, totally arbitrary, and nowhere near what it should be but so far nobody has yet come up with a better one. This rule has changed multiple times and nobody is happy with it but there have been no better ideas put forward. In engineering circles they promote the idea of using EMTP for everything! That’s overkill even for engineers.