That if there is GFP upstream that can "see" a downstream ground fault, then you don't need to protect the feeder again with separate GFP.
An example where this gets messy is if there is GFP on the service and a feeder is derived from a downstream delta-wye transformer (SDS) then the feeder on the transformer secondary is not protected upstream so you need it again if you are above the 1000A and 277V to ground.