Hey everyone,
I'm getting tunnel vision on a potential issue and I'm needing a little guidance. My issue pertains to ground fault selective coordination in healthcare facilities. I have a healthcare facility where I have two levels of ground fault protection, which are required to be coordinated within the system. Normally, the phase curves are coordinated, and the ground fault curves are coordinated separately. However, in cases where a protective device does not have a ground fault trip sensor, a ground fault on its load side will be treated the same as a phase fault. Therefore, it's imperative the phase trip curve be coordinated with the upstream ground fault protection. This is my understanding at least so correct me if I'm wrong.
Most of this equipment is existing so the design is what it is. My scenario has a 4000 amp fuse (480V three phase, four wire) on a switchboard (HMP) that has a feeder breaker of 1200 amps that then feeds over to a main lug only panel (MPP2) with a 600 amp breaker. The 4000 amp fuse and the 1200 amp breaker both have ground fault protection. The 600 amp breaker does not have any ground fault protection as it is not required.
Do I need to coordinate the 600 amp breaker's phase settings with the ground fault sensors on the 1200 amp and 4000 amp overcurrent protection upstream? It's pretty much impossible for me to do given the parameters of the settings on the 600 amp breaker and it would also destroy any coordination that I have with the other phase settings for overcurrent protection downstream.
I have attached a picture of the one line and the time current curves for reference.
I'm getting tunnel vision on a potential issue and I'm needing a little guidance. My issue pertains to ground fault selective coordination in healthcare facilities. I have a healthcare facility where I have two levels of ground fault protection, which are required to be coordinated within the system. Normally, the phase curves are coordinated, and the ground fault curves are coordinated separately. However, in cases where a protective device does not have a ground fault trip sensor, a ground fault on its load side will be treated the same as a phase fault. Therefore, it's imperative the phase trip curve be coordinated with the upstream ground fault protection. This is my understanding at least so correct me if I'm wrong.
Most of this equipment is existing so the design is what it is. My scenario has a 4000 amp fuse (480V three phase, four wire) on a switchboard (HMP) that has a feeder breaker of 1200 amps that then feeds over to a main lug only panel (MPP2) with a 600 amp breaker. The 4000 amp fuse and the 1200 amp breaker both have ground fault protection. The 600 amp breaker does not have any ground fault protection as it is not required.
Do I need to coordinate the 600 amp breaker's phase settings with the ground fault sensors on the 1200 amp and 4000 amp overcurrent protection upstream? It's pretty much impossible for me to do given the parameters of the settings on the 600 amp breaker and it would also destroy any coordination that I have with the other phase settings for overcurrent protection downstream.
I have attached a picture of the one line and the time current curves for reference.