Re: ground fault setting on circuit breakers
I would like to add to Ron's note about there would be trouble with any GFI activated downstream device. Actually, any device, breaker, fuse, etc., that should operate on a ground fault needs to be considered, not just devices with GFI settings.
I have been called to more than a few installations where the ground fault, is set too low, and a simple 20 amp single pole 277 volt lighting breaker is slower than the settings on the main GFI. Even with a main setting of 100 amps or so, you often won't let the 20 amp downstream breaker operate.
Another common problem I encounter is an HVAC compressor motor going bad, and the GFI on the service main will beat the downstream HVAC breaker. I finally convince the Contractor to raise the GFI setting, and all of a sudden the HVAC breaker trips.