Do you typically see a ground fault setting on emergency generator (Diesel type) main breakers? If so are these ground fault settings only intended to alarm or to trip the generator breaker on ground fault?
Ideally in a system with downstream feeders the feeders themselves will have a second level of ground fault and will trip first for ground faults downstream of the feeders. But in a system that does not have ground fault on feeders and only on gen main what is the typical rule of thumb, or what does NEC dictate? Should this breaker alarm only, or trip for downstream ground faults? I don't think you would want it to trip and thus take out the whole emergency system?
What are the typical settings of these ground fault breakers weather they are set to trip or alarm? Do you set them at 1200A with a .3-.5s delay as you would with a utility main?
Is the NEC specific on when a second level of ground fault protection (ground fault on feeders) is required for emergency or normal systems?
Ideally in a system with downstream feeders the feeders themselves will have a second level of ground fault and will trip first for ground faults downstream of the feeders. But in a system that does not have ground fault on feeders and only on gen main what is the typical rule of thumb, or what does NEC dictate? Should this breaker alarm only, or trip for downstream ground faults? I don't think you would want it to trip and thus take out the whole emergency system?
What are the typical settings of these ground fault breakers weather they are set to trip or alarm? Do you set them at 1200A with a .3-.5s delay as you would with a utility main?
Is the NEC specific on when a second level of ground fault protection (ground fault on feeders) is required for emergency or normal systems?