gar
- Ann Arbor, Michigan
- EE
100902-1949 EST
nhfire77:
If you have addressable devices this probably means there is some sort of data signal sent out on the signaling wires.
What does "monitored side of a addressable input module" mean? Is this the wire you said is the negative side of the data loop? How does this monitoring wire monitor whatever it monitors?
Keep in mind that my comments on the ground fault detection is only conjecture. The greatest use of this discussion may be to stimulate other ideas.
In your first post you said:
You went on to say:
Next you said:
nhfire77:
So this was with the pair of signal wires to the loop that has a problem disconnected from the FACP. Did you try a normal DVM resistance check? This is not more than a few volts.When metering the one side of the leg that I believe is the problem, no ground fault is detected (about 26 Meg Ohm actually, the other three legs are similar in readings not causing a GF, the threshold for GF in the panel is 40K Ohm)
You went on to say:
How long may the ground fault condition remain. A few seconds, minutes, or hours?When it is attached to the FACP, the GF condition returns. However, it randomly goes away, so right now its normal.
Next you said:
This might mean the megger voltage is sufficient to blow or heat away the ground fault.When this occurs and the GF condition is present on the panel but not on my meter, typically the GF is on the monitored side of a addressable input module (kinda like the load side of a circuit, but not.)