I'm an Electrical Engineering student, and working as an Electrician intern for a drilling company this summer. The rigs are run primarily on 600 volt and 480 volt AC power. Just the other day, we had a ground fault on the rig, and got readings of 0-480-480 volts on the phases between the phases and ground. I understand that, because the first phase is going to ground, you sense the first phase added to the second two phases when reading voltage from phase to ground. I have two different questions, that had mixed answers from some of the electricians:
Question 1: If you reached out and touched the phase with 0 volts, (the phase that has the ground fault), would it kill you? Or even shock you at all? The electricians said that it would definitely kill you, but I don't understand how this is possible. If the multimeter is sensing the voltage from the power lug to ground, and it reads 0 volts, if we touch the power lug, and our feet are grounded on the rig floor, which is grounded, shouldn't we have 0 volts across our body, and not be hurt in the least?
Question 2: With this ground fault, and readings of 0-480-480 volts on the phases, the 3 phase motors on the shakers and pumps ran perfectly fine! Not a problem at all. How can a 3 phase motor run on power that only has 2 phases? I understand how AC motors work, and I would understand it if the motors ran a little bit, but were bogged down and slow, but these motors run 100% fine.
For goodness sake, this is driving me crazy. Someone please give me some insight on this! Thanks!
Question 1: If you reached out and touched the phase with 0 volts, (the phase that has the ground fault), would it kill you? Or even shock you at all? The electricians said that it would definitely kill you, but I don't understand how this is possible. If the multimeter is sensing the voltage from the power lug to ground, and it reads 0 volts, if we touch the power lug, and our feet are grounded on the rig floor, which is grounded, shouldn't we have 0 volts across our body, and not be hurt in the least?
Question 2: With this ground fault, and readings of 0-480-480 volts on the phases, the 3 phase motors on the shakers and pumps ran perfectly fine! Not a problem at all. How can a 3 phase motor run on power that only has 2 phases? I understand how AC motors work, and I would understand it if the motors ran a little bit, but were bogged down and slow, but these motors run 100% fine.
For goodness sake, this is driving me crazy. Someone please give me some insight on this! Thanks!