Ground faults and capacitance

Status
Not open for further replies.

K2500

Senior Member
Location
Texas
I have a high resistance grounded 277/480 system. Ground fault detection shows ground fault of about .8A.

Fault level shows no change with pulser activated.
Mostly small motor loads, plus four 100HP VFD's.

Could this be a calibration issue with the detector, sensing capacitive charging current, or is there something else I should be looking for?

Equipment is Cutler Hammer, C-HRG.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
110501-1510 EDT

277 V at 0.8 A would be an Xc = 346 ohms. At 60 Hz this would result from a capacitance of 7.6 mfd. Quite large for leakage capacitance of wiring over a short range. Actually gigantic.

.
 