GizmoBreaker
Member
- Location
- New York City
I have been asked to install a new 200A switch in an existing commercial building. The switch will mount adjacent to 2 existing 200A switches and be used by persons who rent the space on a temporary basis for photo shoots and the like.
The service entrance is in another room, separated by a common wall, but the service equipment is about 40 pipe feet away from the raceway that supplies the 2 existing switches.
The GEC connects both to a ground rod under the service equipment and to the water main, which is in the same room as, and only 6' away from, the raceway and the 2 200A switches. There is no ground conductor run in the pipe that feeds the switches and I cannot install one without pulling the existing wire out.
Because the new switch will supply temporarily installed equipment that uses 3 phases, 1 neutral and 1 ground, I need to install a ground connection in the switch. I am reluctant to rely solely on the conduit path back to the service. As noted, above, I can't squeeze another wire into the existing conduit. If I install a new #6 GEC to the water pipe, only, will I be in compliance? I cannot drive a rod near the switch as there is no earth directly under the foundation and no access to the space below.
And:
Will I have a ground loop problem with any electronic equipment that might be used?
Thanks, everyone, for any guidance you can provide.
Marty
The service entrance is in another room, separated by a common wall, but the service equipment is about 40 pipe feet away from the raceway that supplies the 2 existing switches.
The GEC connects both to a ground rod under the service equipment and to the water main, which is in the same room as, and only 6' away from, the raceway and the 2 200A switches. There is no ground conductor run in the pipe that feeds the switches and I cannot install one without pulling the existing wire out.
Because the new switch will supply temporarily installed equipment that uses 3 phases, 1 neutral and 1 ground, I need to install a ground connection in the switch. I am reluctant to rely solely on the conduit path back to the service. As noted, above, I can't squeeze another wire into the existing conduit. If I install a new #6 GEC to the water pipe, only, will I be in compliance? I cannot drive a rod near the switch as there is no earth directly under the foundation and no access to the space below.
And:
Will I have a ground loop problem with any electronic equipment that might be used?
Thanks, everyone, for any guidance you can provide.
Marty