How do I determine size of building steel ground and neutral bonding jumper for 112.5 KVA transformer?
Have you read through art 250 part II? Some places will direct you to other parts of the code as well, like your building steel will require you to see 250.66
I suggest you do that first then ask more specific questions if you have them.
You size it to the conductors connected to the separately derived system - which is the secondary. Note it is based on secondary conductor size and not size of transformer, which means you could possibly have either of:So lets say I have a single set of 3/0's for my primary into transformer and parrallel 250's for secondary (AL). Would I size my building steel ground for the transformer to the primary's and go with #6 copper, or would I have to size it for the parrallel 250's?