What he is saying is that the signal conductors are not considered as having any relation to the EGC of the power circuits. The signal handling components will typically be bonded to ground/earth/EGC as part of the circuit supplying power to them. That means that there is usually no need for an EGC in the conduit containing the signal conductors.
All of the power circuits are in one conduit, so that conduit must act as (raceway EGC) or contain (wire EGC) an EGC functionality suitable for the size of the largest of those circuits.
If you had two conduits, each containing power conductors, then you would need to consider how the EGC is provided for each independently.
In the special case that the conduits contain parallel conductors of the same circuit you will need to calculate the wire EGC size based on the total equivalent sized single wire circuit and then put a correspondingly sized EGC in both conduits.