I believe that I have put this incident in a thread some time ago. I feel that it is important enough to discuss it again.
This incident happen in 1965, when I became a 1st Line Electrical Supervisor for the Dupont Company.
We have on the plant a 2300 volt, 3-phase, ungrounded system, with the three lights at the sub-station. The primary voltage is 11000 volts, and the secondary 2300 volts.
I received a call from our Power department and they informed me that one of my lights was out.
Now, it was my job to go with an electrician and find the ground, before we get another ground in a different phase, then you will have a problem.
Our procedure was to go and shut down 2300 volt motors, and open up the 2300 volt disconnects.
Almost 100 percent of the time, we would find the ground in a motor.
Well, we proceeded to do this, when we came to a building and told the operations that we needed to shut down their 2300 volt motor, and they informed me that they needed to start up another motor before they could shut down the motor that I asked for.
Well, unbeknown to us, the motor that the operator started up, had a ground in another phase, and we had a big electrical explosion out at the sub-station.
This is a lesson that I will never forget, and I took a lot of ribbing from my fellow electricians of how not to check for a 2300 volt ground.
I know that this was lengthy message, but I felt that I wanted to pass it along.