Howdy - is it a problem that ground and line are tied together?

I put a meter on the service line (before breaker) and placed the other probe on ground and the meter read 118VAC?

Checked a few receptacles and saw the same? Many thanks for suggestions on how to trouble shoot this one.

David
 

Twoskinsoneman

Senior Member
Location
West Virginia, USA NEC: 2020
Occupation
Facility Senior Electrician
Howdy - is it a problem that ground and line are tied together?

I put a meter on the service line (before breaker) and placed the other probe on ground and the meter read 118VAC?

Checked a few receptacles and saw the same? Many thanks for suggestions on how to trouble shoot this one.

David

A indication of 118vac of potential between the service ungrounded conductor and ground does not mean they "tied" together.
 

c_picard

Senior Member
Location
USA
If they were "tied" together, you would get zero volts, among other things...
 