Greetings, we are designing a CNG bus maintenance facility where I am specifying a ground loop around the facility as per NFPA 780 7.3.7.1:
"7.3.7.1 A ground ring electrode or ground loop conductor
supplemented by grounding electrodes as identified in 4.13.2
through 4.13.7 shall be provided for structures containing
flammable vapors, flammable gases, or liquids that can give off
flammable vapors."
However, one electrical designer on the design team is stating that the ground loop around the facility is not required. Here is what he is stating, which I think is incorrect:
"No fueling in the building. The only flammable gases are inside a gas tank of a vehicle and therefore no grounding loop is required because a vehicle is not part of the building. This is an additional cost that is not required nor is needed. If there were flammable vapors, gases then it would require by code (1) loop for lightning and (1) loop for grounding".
Any feedback from those who have designed such facilities would be appreciated.
"7.3.7.1 A ground ring electrode or ground loop conductor
supplemented by grounding electrodes as identified in 4.13.2
through 4.13.7 shall be provided for structures containing
flammable vapors, flammable gases, or liquids that can give off
flammable vapors."
However, one electrical designer on the design team is stating that the ground loop around the facility is not required. Here is what he is stating, which I think is incorrect:
"No fueling in the building. The only flammable gases are inside a gas tank of a vehicle and therefore no grounding loop is required because a vehicle is not part of the building. This is an additional cost that is not required nor is needed. If there were flammable vapors, gases then it would require by code (1) loop for lightning and (1) loop for grounding".
Any feedback from those who have designed such facilities would be appreciated.