WOW, what a coincidence. I received a phone call this morning around 3:00 am informing me one of our telephone switch offices was struck by lightning, and the AC service was out and the switch was not processing calls. The switch serves all the cell sites in Eastern Oklahoma and Western Arkansas. More on that in a moment.
Karl, yes I do use a gauze meter to investigate noise problems. In a telephone office all the DC grounding conductors are run in open air and not paired with any associated power conductors. Since most of the ground systems are isolated single point, they act as antennas, and induced currents are a problem from time-to-time. I find the gauze meter useful if the induced current is from the AC power system. Occasionally some installer runs a ground conductor too close to a florescent light or motor or something and the gauze meter easily identifies the source of the induction. I do not find it useful for high frequency noise; use other test equipment for that.
Back to the lightning strike. I have spent the last 15 hours bringing one of our telephone offices back on line, whew! When I arrived I found the class C TVSS at the service entrance completely blown off the wall, generator transfer switch control board fried, transformer fuses blown, 48 volt rectifiers AC breakers tripped, UPS batteries dead, and worst of all the switch was not processing calls. The TVSS, generator transfer switch control board, transformer fuses, rectifier AC breakers, and UPS were easy to diagnose and fix. Returned service by 6:00 am.
Although the switch still had power from the battery plant it was not processing calls. Once we recovered the UPS we were not able to communicate with the switch via the terminals located throughout the building. The terminals are powered from the UPS on IGR.
After a few hours we replaced the I/O RS-232 cards that interface the terminals with the switch. I investigated the ground system on the switch to try to determine how lightning entered the switch. The switch uses a ground window and single point grounding to prevent any outside faults from flowing through the isolated ground plane. I did not find any violations with the external grounding. Then it occurred to me the RS-232 uses a ground wire as a reference for transmit and receive data. The light went off in my head. I looked at the cables and they were metallic, rather than optical, problem found.
I looked closely at the RS-232 cards that were replaced, and found the ground and power circuit board traces burnt into, problem confirmed. To enlighten you, the problem is the switch is served by DC power from a ground window where all grounds originate to form a single point isolated ground. Then the switch and all its components are kept completely isolated from any incidental contact with ground by using isolation techniques. The RS-232 cables serve multiple terminals and desktop computers located through out the facility. The terminals and desktops are powered from the UPS on IGR. This corrupted the isolated ground plane and introduced a GROUND LOOP, which allowed lightning current to flow through the isolated ground plane.
When I showed and explained the problem to operations personnel they were stunned. They assumed since they were using IGR they were safe, wrong, dead wrong. There are two solutions to the problem. 1 is to install and inverter in one of the switch frames and reference its output to the ground window, or 2 install optical isolators on the RS-232 cables. The optical isolators were ordered today!