zbang:
Why shouldn't we talk about fault conditions? They occur and most likely cause physical damage rather than just data errors.
Disregarding faults there are still ground path problems relative to noise.
In a no-fault situation, if all the EGCs are properly tied together and assuming that the data reference is tied to the EGC, then as I said, there shouldn't be any problems data-wise. OTOH, running a ground-referenced signal outside of the immediate area is usually asking for trouble. Five racks down ought to be OK, 500' across a factory floor might work for a while.... I did have an installation that ran rs-423 between the 1st and 10th floors of a building, and we didn't have problems, but we had pretty solid grounds everywhere and were only running 9600bps for terminals and printers.
Here is a real world example:
Two HAAS VF-3 CNC machines located side by side, physically 4 feet between them. There was about 1.5 years age difference. One machine used DC servos and the other brushless servos. Both were fed from the same bus duct, 240 V delta, and both were grounded by the EGC ground bus. Additionally each machine had a supplemental ground rod. A separate RS232 cable was run from each machine to a common computer. Computer to CNC distance across the floor was about 50 ft. Cable lengths were about 120 ft, high ceilings.
With servos off communication to both machines was OK, but limited to about 9600 baud. This was cable length dependent. In DNC mode the machine with brushless servos had an error rate so high that no effective communication was possible in either direction. Switching the cables between the machines made no difference. The measured voltage with a Fluke 87 in AC position between the enclosures of the two machines was about 4.5 V with the servos on. The noise probably approximates a Gaussian distribution and therefore peaks would be substantially higher than 4.5 V.
Another observation was by the HAAS serviceman that with his laptop operating on batteries and no AC power cord connection there was no communication problem.
Installation of our I232 isolator system solved the noise problem and allowed the user to work at 115.2 kbaud. With this system you could add a 1000 V 60 Hz common mode signal to the computer and while present communicate without error.
To depend upon a low impedance ground path to avoid ground path noise problems still leaves you with a marginal system compared with using some form of isolation.
iwire:
What is the definition of a modern method?
As I had pointed out copper based Ethernet is most likely to include transformer isolation. This should not experience any problem from normal ground path noise or normal faults.
RS232, 422, and 485 are still common communication interfaces and all are limited to moderately low common mode voltages.
.