Re: ground lugs in transformer
Based on last sentence of 250.30(A)(2)(a) which sends us to 250.24(A)(4); if the GEC does not terminate at XO, I ask for a double lug mounted to the enclosure or two lugs under one bolt.
edit add: Also the last sentance of 250.30(A)(1) requires the bonding jumper to connect to the same point as the GEC.
As far as the equip grds, 250.130 sends us to 250.30(A)(1). There the code tells us to connect the equip grd conductors to the grounded cond. with the bonding jumper. I think this is where the inspector is getting the one bolt interpretation.
How the bonding jumper connects the equip grd cond's is not really clear to me.
Can anyone help me see what I might be missing here? 250.24(A)(4) would suggest the the intent is a equip grd terminal bar.
I have asked for the double lug set up in my first paragraph and allowed equip grd cond's to connect to the bonding jumper via the enclosure. Paint scraped of course and full metal to metal contact, meaning not using the vent openings for holes for the bolts.
Perhaps 408.20 should be extended to all enclosures and equipment where grounding conductors are provided? If that is what the code has in mind.