Hey guys. 17 yrs in this trade, looking for ideas...
1800a service at 480Y...490V on A B and C to utility neutral...after the main, I’m getting weird voltages to ground...A-N 465V. B-N 475. And 485V C-N. It also varies quite a bit. I’m also getting 14.5-15.5 volts from after the main neutral to my building steel, and concrete grounding Electrode. I also get 0.2 amps on these ground. I’ve checked my building steel connection and other ground on MAIN. all seems good and at both locations and all the lugs and bus bolts and other breakers have been torqued on a recent shut down at all main gear..
what is strange and the other guys say it’s fine, is in getting a decent ark in my 480v panels when I go N to ground with my screw driver...I know there is something up with the neutral..any ideas? Lights keep burning out, power packs keep burning up LCP trans smoked...
Any other things I should check? I haven’t contacted the utility company yet because they are giving me nice clean power..
All my 120/208 (through trans) see no issue. (Bonded to building steel as well)
Thanks I’m Advance.
1800a service at 480Y...490V on A B and C to utility neutral...after the main, I’m getting weird voltages to ground...A-N 465V. B-N 475. And 485V C-N. It also varies quite a bit. I’m also getting 14.5-15.5 volts from after the main neutral to my building steel, and concrete grounding Electrode. I also get 0.2 amps on these ground. I’ve checked my building steel connection and other ground on MAIN. all seems good and at both locations and all the lugs and bus bolts and other breakers have been torqued on a recent shut down at all main gear..
what is strange and the other guys say it’s fine, is in getting a decent ark in my 480v panels when I go N to ground with my screw driver...I know there is something up with the neutral..any ideas? Lights keep burning out, power packs keep burning up LCP trans smoked...
Any other things I should check? I haven’t contacted the utility company yet because they are giving me nice clean power..
All my 120/208 (through trans) see no issue. (Bonded to building steel as well)
Thanks I’m Advance.